Anyone else see there AirFiber 24 using 100W?
WS-12-250-DC on Frimware 1.4.6
Chris
AirFiber 24 pulling 100W??
- htsinc
- Member
- Posts: 8
- Joined: Tue Mar 07, 2017 3:35 pm
- Has thanked: 0 time
- Been thanked: 0 time
- Julian
Re: AirFiber 24 pulling 100W??
sounds more like ground current blew your current sensor.. try switching ports, if the draw returns to normal, it's a safe bet that's what happened.
It's not actually possible for a port to deliver 100w, things start to break fairly quickly.
It's not actually possible for a port to deliver 100w, things start to break fairly quickly.
-
sirhc - Employee
- Posts: 7422
- Joined: Tue Apr 08, 2014 3:48 pm
- Location: Lancaster, PA
- Has thanked: 1609 times
- Been thanked: 1326 times
Re: AirFiber 24 pulling 100W??
Most common reason for current sensors to get blown are from excessive ground current where your AC power ground rods are not bonded to your tower ground rods.
Here are some good posts on grounding:
viewtopic.php?f=30&t=1816
viewtopic.php?f=30&t=188
viewtopic.php?f=30&t=1429
viewtopic.php?f=17&t=1786&start=30#p13447
https://community.ubnt.com/t5/airFiber/ ... rue#M31070
We can repair current sensors if you RMA it but if you do have a ground issue and you do not fix it more damage will occur.
Rain events are most common reason to cause ground potential shifts.
If your electrical service ground rods are in poor condition and your tower ground rods are in good condition and it rains then the electrical service ground rods degrade and the best path to earth ground then is the tower ground rods so all that ground current flows through the switch and across the Ethernet cables.
I would check your grounding and RMA that unit for repair.
Here are some good posts on grounding:
viewtopic.php?f=30&t=1816
viewtopic.php?f=30&t=188
viewtopic.php?f=30&t=1429
viewtopic.php?f=17&t=1786&start=30#p13447
https://community.ubnt.com/t5/airFiber/ ... rue#M31070
We can repair current sensors if you RMA it but if you do have a ground issue and you do not fix it more damage will occur.
Rain events are most common reason to cause ground potential shifts.
If your electrical service ground rods are in poor condition and your tower ground rods are in good condition and it rains then the electrical service ground rods degrade and the best path to earth ground then is the tower ground rods so all that ground current flows through the switch and across the Ethernet cables.
I would check your grounding and RMA that unit for repair.
Support is handled on the Forums not in Emails and PMs.
Before you ask a question use the Search function to see it has been answered before.
To do an Advanced Search click the magnifying glass in the Search Box.
To upload pictures click the Upload attachment link below the BLUE SUBMIT BUTTON.
Before you ask a question use the Search function to see it has been answered before.
To do an Advanced Search click the magnifying glass in the Search Box.
To upload pictures click the Upload attachment link below the BLUE SUBMIT BUTTON.
3 posts
Page 1 of 1
Who is online
Users browsing this forum: No registered users and 18 guests