I know you said you find you have better luck with the ESD cable but this is probably because you do not have a sufficient dedicate ground on all your towers to all your radios all bonded together?
Now I am not saying people should not use ESD cable because they SHOULD however most of my towers were put in before ToughCable came out and I ran normal indoor FTP cable in plastic and metal conduits between my ground cabinet and a top side NEMA cabinet. I often ran 24 wires and used 66 Block punch downs at top and bottom so I had 24 wires pre-run and ready for expansion and as you all have seen I put a lot of radios on a tower.
I have a main ground bus at the base of the tower that connect to all the tower ground rods.
I have a ground bus in my ground cabinet that is connected to the main tower ground bus with #2
I have a #2 bond wire from the main tower ground bus and the electric service ground rods.
I have a #2 bond wire from the ground cabinet ground bus to the electric service ground rods
I have #2 that runs up the tower from the main tower ground bus to a ground bus where my antennas are located.
I have a #6 bond wire from the upper ground bus to each antenna
I have a #6 bond wire from the upper ground bus to the upper NEMA tower mounted cabinet
Anyway the reason you probably see better luck with the ESD cable is because of the copper ESD drain wire in the ToughCABLE is taking some of the current off your data lines where as my grounding system wires is doing that for me.
If you read this post you will find the exert below in that post which is another reason I hate Ethernet surge protectors and how a ground potential difference can cause Ethernet Errors.
viewtopic.php?f=30&t=1816&p=13625#p13625
Data-line surge suppressors operate by "clamping" the data line to ground whenever the voltage exceeds a certain level. After the transient surge has passed, the suppressor turns off, allowing normal data traffic to resume. Data-line surge suppressors should be connected right at the network port of the equipment being protected. The suppressor ground strap should be connected only to the equipment chassis. This ensures that there is no potential difference between the suppressor ground and the equipment ground when a transient surge is being suppressed. For this reason, data-line surge suppressors that connect to ground at the receptacle are not as effective. When installing data-line surge suppressors, they should be used in pairs to protect the equipment at each end of the cable.
Several misconceptions persist about how to use data-line surge suppressors. Ironically, some of these originate with manufacturers.
- Data-line surge suppressors do not prevent noise from interfering with or corrupting data. If the voltage on the data cable is high enough to trip the suppressor, then the data is already corrupt.
- Data-line surge suppressors do not prevent ground loops from corrupting data for the same reason.
- Data-line surge suppressors are the wrong choice when a steady-state ground potential difference exists.
If the ground voltage exceeds the suppressor trip voltage, the data line will be continuously clamped to ground. If the ground voltage is high enough, the continuous current diverted to ground will burn open the suppressor. A properly designed suppressor will interrupt the data flow when its circuits become damaged. In any event, using a surge suppressor in this application will not restore data transmission.