scott@airgrids.com wrote:Sirhc. I did use a 100' 12/3 extension cord for power to the switch/tower. I didn't change the ground to the local tower earth ground as you described - so that likely didn't help. I will tie the earth ground as you suggest and run the tests above in a few days when I get back to the tower. I'll update then. THX.
Yea what happens is Earth Ground Current will try to equalize between the 2 grounding systems and the path of this current looks like this:
EARTH GROUND===[Electric Service]===100' cord===[cabinet + switch]=====Ethernet Cable====[Tower]===EARTH GROUND
Now no matter which side has the better ground the current will try to equalize and flow THROUGH your switch. - NOT GOOD
Very possible you have damaged your switch, I would bench test it as I outlined above.
So many people think Ground is Ground and they could not be further from the fact/truth.
Keep in mind that any AC equipment located on the electric service wants to clamp excessive voltage/current to Earth Ground so if the Earth Ground is better at the tower then all the excessive voltage/current will flow through that 100' cords to and through your switch to get to the tower Earth Ground.