Tue May 23, 2017 11:13 am

From your guys experiences, what is the best site UPS to use? We've had two APC Pro 1000 go out on us in locations where the power never really goes out but some time flickers.

User avatar
sirhc
Employee
Employee
 
Posts: 7415
Joined: Tue Apr 08, 2014 3:48 pm
Location: Lancaster, PA
Has thanked: 1608 times
Been thanked: 1325 times

Re: UPS

Tue May 23, 2017 11:55 am

UPS needs to be sized twice the size as needed to cover in rush or the UPS needs to specify it can handle in rush demand up to 2x its rating.

So for instance our 250W switch needs a UPS rated at 500W or the UPS needs to say it can handle in rush to 2X its rating then you could use a 250W UPS but keep in mind you need to add up all your devices and size to 2X that size.

It does not matter that you will not power 250 watts without switch the 250W power supply will use close to 500W in rush for a very short time during the inrush.

Personally most WISPs have stopped using drycell computer UPS systems for AGM Battery Inverter Chargers like the TrippLite units

I use the 1250W versions
https://www.walmart.com/ip/Tripp-Lite-P ... 3=&veh=sem
Support is handled on the Forums not in Emails and PMs.
Before you ask a question use the Search function to see it has been answered before.
To do an Advanced Search click the magnifying glass in the Search Box.
To upload pictures click the Upload attachment link below the BLUE SUBMIT BUTTON.

Return to The Lounge

Who is online

Users browsing this forum: No registered users and 25 guests