High current reading on port

Mon Aug 09, 2021 10:14 am

Screen Shot 2021-08-09 at 10.06.31 AM.png


I've had a WS12DC switch installed now for about 12 months powering a Mini6 with 48VH. The Mini6 is located about 12 feet away. The Mini6 then powers a single AP via POE. The other devices on the mini6 are non-poe.

I noticed today while adding an additional Mini6 to my network that the port on the WS12DC powering the Mini6 reports 80+ watts. This is incorrect. The mini6 itself only reports using a total of 15-20W. Also I confirmed with a clamp on amp meter the total power being used by the WS12DC is less than 50W. If I move the Mini6 to another port on the WS12 the power reading is correct. The incorrect power reading appears to be tied to the port.

I've searched the forums. Other issues similar to this appear to be related to tower installations which this is not. Any chance this is a firmware issue?

User avatar
Stephen
Employee
Employee
 
Posts: 1033
Joined: Sun Dec 24, 2017 8:56 pm
Has thanked: 85 times
Been thanked: 181 times

Re: High current reading on port

Mon Aug 09, 2021 11:18 am

terbonium wrote:Any chance this is a firmware issue?


Not unless your switch is running on old firmware, if it's not on the latest you can get it here: viewtopic.php?f=17&t=240

But it's much more likely you've got a damaged current sensor. You can go to https://rma.netonix.com/ to start an RMA to have it repaired if you wish.

terbonium
Member
 
Posts: 7
Joined: Tue May 26, 2020 11:50 am
Has thanked: 0 time
Been thanked: 0 time

Re: High current reading on port

Wed Aug 18, 2021 9:33 am

Screen Shot 2021-08-18 at 9.30.47 AM.png


Thank you for the info. I've moved the Mini6 to another POE port(port 3), current sensor readings there are correct. I've moved a non-poe device to the port w/ the incorrect current sensor readings(port 1). Is there much risk of further failure on this port if I delay repair?

User avatar
Stephen
Employee
Employee
 
Posts: 1033
Joined: Sun Dec 24, 2017 8:56 pm
Has thanked: 85 times
Been thanked: 181 times

Re: High current reading on port

Wed Aug 18, 2021 1:46 pm

To the best of my knowledge, no it shouldn't. PoE should work fine without the sensors, it just can't tell you reliably what the power output is on that port.