We're trying to design a "micropop in a box" solution that will include a Netonix DC switch, 1-2 airfiber 5 (or 3 or 2)X backhauls, and up to 3 rockets. I'd like to be able to have at least a little battery backup for the system, preferably at 48V.

An suggestions on the UPS component? I've used meanwell DR-UPS-40 plus 24V power supplies in the past with pretty good success, but that's not 48V. Tycon's 48V battery charger / ups looks interesting but takes up a lot of space. Other thoughts we've played with include using a 48V power supply plus a 48V solar charge controller.

Any success stories or other ideas?

User avatar
sirhc
Employee
Employee
 
Posts: 7421
Joined: Tue Apr 08, 2014 3:48 pm
Location: Lancaster, PA
Has thanked: 1609 times
Been thanked: 1326 times

Re: Micropop UPS

Wed Sep 30, 2015 2:06 pm

If you use a WS-12-250-DC your batteries can be between 9-60V and still power 24V and 48V devices and you do not need conditioned power.
Support is handled on the Forums not in Emails and PMs.
Before you ask a question use the Search function to see it has been answered before.
To do an Advanced Search click the magnifying glass in the Search Box.
To upload pictures click the Upload attachment link below the BLUE SUBMIT BUTTON.

User avatar
Travis_WVN
Member
 
Posts: 14
Joined: Fri Oct 09, 2015 6:14 pm
Location: Oregon, USA
Has thanked: 13 times
Been thanked: 2 times

Re: Micropop UPS

Tue Nov 10, 2015 3:30 am

I'm having good results with the Powerstream 48V DIN-Rail mounted units. AC to DC48V, with battery backup option!
http://www.powerstream.com/48V-backup.htm

User avatar
rcosby
Member
 
Posts: 28
Joined: Tue Sep 23, 2014 2:02 pm
Has thanked: 0 time
Been thanked: 4 times

Re: Micropop UPS

Tue Nov 10, 2015 3:49 pm

I checked on that UPS, but they said they had a bad batch and the voltages wouldn't adjust correctly.

What is the difference between that and a normal 48v din rail power supply?

User avatar
sakita
Experienced Member
 
Posts: 206
Joined: Mon Aug 17, 2015 2:44 pm
Location: Arizona, USA
Has thanked: 94 times
Been thanked: 80 times

Re: Micropop UPS

Thu Nov 12, 2015 12:45 pm

sirhc wrote:If you use a WS-12-250-DC your batteries can be between 9-60V and still power 24V and 48V devices and you do not need conditioned power.


When it comes to keeping the equipment size down, that voltage flexibility is very nice. :cool:

Meanwell DRC-100A + 1 @ 12V battery = good enough for a low-power site.

https://www.meanwell-web.com/en/product ... t/DRC-100A

We looked at 24V and 48V solutions (including Powerstream) but for the application we're doing having a single 12V battery helps make it all fit in the box. IIRC, the batteries we're using are Alpha 85GXL-HP which gives us plenty of run-time if the power goes out.
Today is an average day: Worse than yesterday, but better than tomorrow.

User avatar
rcosby
Member
 
Posts: 28
Joined: Tue Sep 23, 2014 2:02 pm
Has thanked: 0 time
Been thanked: 4 times

Re: Micropop UPS

Mon Nov 16, 2015 2:34 pm

I agree that battery will give you lots of run-time. But how long does it take to recharge a battery that size with that small of a power supply, allowing enough power for your equipment?

User avatar
sakita
Experienced Member
 
Posts: 206
Joined: Mon Aug 17, 2015 2:44 pm
Location: Arizona, USA
Has thanked: 94 times
Been thanked: 80 times

Re: Micropop UPS

Mon Nov 16, 2015 6:28 pm

How long it takes to recharge depends on how long you run it down and how much of the 100W capacity you are using. :smile:

Seriously though, I haven't formally tested it. We should have decent charging output as we're typically only using 35W or so.

In your case, 2 @ AirFiber could be 36W to 51W by themselves. Add in 3 rockets and that's another 24W. Add about 8W for the switch.

So, your talking < 70 to > 80W right off-the-bat. You'd be close to the edge power-wise so it could be a long recharge if it can handle it at all.

In our case, we're typically 35W to 50W which allows plenty of temperature de-rating as well as recharge current.

Maybe Meanwell will come up with a 200W version.
Today is an average day: Worse than yesterday, but better than tomorrow.

User avatar
rcosby
Member
 
Posts: 28
Joined: Tue Sep 23, 2014 2:02 pm
Has thanked: 0 time
Been thanked: 4 times

Re: Micropop UPS

Mon Nov 16, 2015 8:01 pm

I've made pretty good headway on our micropop box.

I'm using a 240W (5A) 48V power supply with four 12AH batteries and limit our load to ~100W.

Someone smarter than me recommended I don't put more load on than 20% of our battery AH capacity. In other words, if I use 12AH of battery, I should only allow 20% of 12A = 2.4A or 115W of load. I'm estimating about 2.5 hours of run-time if I try not to ruin my battery by going too low. I will use the netonix port shutdown features as a "LVD."

User avatar
sakita
Experienced Member
 
Posts: 206
Joined: Mon Aug 17, 2015 2:44 pm
Location: Arizona, USA
Has thanked: 94 times
Been thanked: 80 times

Re: Micropop UPS

Wed Nov 18, 2015 12:03 am

So what power supply are you using?
Today is an average day: Worse than yesterday, but better than tomorrow.

User avatar
rcosby
Member
 
Posts: 28
Joined: Tue Sep 23, 2014 2:02 pm
Has thanked: 0 time
Been thanked: 4 times

Re: Micropop UPS

Wed Nov 18, 2015 12:24 am

MeanWell SDR 240-48